Fake temp Down Alert
We bought environment control sensor version of ServersCheck and been running from last couple months. I received a message say (TEMPERATURE Thu May 29 08:31:16 2008 OK DOWN 59.36 UNKNOWN) and when I personally check the server room temp, its running fine. Please contact me back to resolve this issue
This discussion has been closed.
Comments
When you click on TEST SETTINGS, what result does it return for that monitor?
What are the settings of your sensors:
- retry interval?
- retries?
- retry interval when down?
The settings of the sensors are follows:
retry interval = 5 sec
Retries = 120 sec
Retries when down = 120 Sec
retry interval : 120 sec (min)
retries: 3
retry interval when down: 120 sec
What do you mean with it keeps getting into a loop? The TEST SETTINGS should open a new window
Can you please disconnect the sensor and reboot the server and then reconnect the sensor?
Temp in room is okay.
I checked email notification , that is working fine.
when ever i try to test the settings, its keep doing something and doesn't give me any results.
sensor_check -L log.txt -C COM 9
Replace 9 with the actual com port
Reply with the output being returned.
Send screen captures of the test settings and settings to [email protected] - attn Eric.