Problem with Networked Temp Sensor
I need help with initial setup.
I followed the Quick Installation Guide-Networked Sensor to the letter. When configuring the ServersCheck Montoring Software for sensor communication at the stsep where you set the temperature settings, I click on the "Test Settings" button and receive the following error:
Status: DOWN?
Error returned: Value could not be retrieved from sensor
Can anyone help?
I followed the Quick Installation Guide-Networked Sensor to the letter. When configuring the ServersCheck Montoring Software for sensor communication at the stsep where you set the temperature settings, I click on the "Test Settings" button and receive the following error:
Status: DOWN?
Error returned: Value could not be retrieved from sensor
Can anyone help?
This discussion has been closed.
Comments
If so, then enter following in the command prompt (in the agents subdirectory):
sensor_check -L log.txt -C TCP IP:3001
It will generate a file called log.txt; open it and reply with the output.
On our 2nd sensor, we are receiving the following:
Status: DOWN?
Error returned: No connection could be made because the target machine actively refused it
For the second sensor, I assume that DS202 settings are 100% identical compared to the first one.
If so, is there a firewall in between that could block port 3001?
C:Program FilesServersCheck_Monitoringagents>sensor_check -L log.txt -C TCP 172.16.100.122:3001
No connection could be made because the target machine actively refused it
With regards to ServersCheck, when we select "Start Monitoring", the server seems to hang. What is the normal wait time for the server to report back that monitoring has started?
Start the service from the Windows Service Manager.
The service is called "ServersCheck Monitoring"
Have you performed an upgrade of the software or directly installed it off the web?