Problem with IO Dry Contact module
Hallo all
We have a problem with I/O and I think I know why but need your confirmation.
if we connect the I / O module with the BASE-WIRED and an additional sensor, the I / O module hangs up irregularly.
If we connect the I / O module to the BASE-WIRED without an additional sensor but use a cable length of more than 3 meters for the DRY contacts, it can also happen that no status is recognized
If this is so correct, we can actually only use the I / O module in connection with a BASE-Wired and a maximum length of 3 meters, without an additional sensor
We have a problem with I/O and I think I know why but need your confirmation.
if we connect the I / O module with the BASE-WIRED and an additional sensor, the I / O module hangs up irregularly.
If we connect the I / O module to the BASE-WIRED without an additional sensor but use a cable length of more than 3 meters for the DRY contacts, it can also happen that no status is recognized
If this is so correct, we can actually only use the I / O module in connection with a BASE-Wired and a maximum length of 3 meters, without an additional sensor
Comments
You may also check the connection of the RJ45 cable connected from your IO Sensor to your Base Unit.
I have tried to set up a wire on one of the IO dry contact inputs with more than 3-meter length and short the end of the wire and I can see the trigger response on the IO Sensor. You may also try to set the sensor polling time to 1 second.