SNMP OIDs needed for Smoke and Leak on MultiSensor HUB EXP-4HUB
Hardware Version
Release 5.1
Firmware Version
Release 8.6
SENSORS
Leak - Connected on MultiSensor & Hub "Leak" ethernet port
Smoke - Connected on MultiSensor & Hub "Input 1"
Both work via web GUI, snmpwalk only seems to dump info about the BASE-WIRED SensorGateway, not the hub attached to it, see below:
snmpwalk -v2c -t 1 -c public 172.16.170.9
SNMPv2-MIB::sysDescr.0 = STRING: Temperature & Sensor Gateway
SNMPv2-MIB::sysObjectID.0 = OID: SNMPv2-SMI::enterprises.17095
DISMAN-EVENT-MIB::sysUpTimeInstance = Timeticks: (34217334) 3 days, 23:02:53.34
SNMPv2-MIB::sysContact.0 = STRING: http://www.serverscheck.com
SNMPv2-MIB::sysName.0 = STRING: BRD DC SensorGateway
SNMPv2-MIB::sysLocation.0 = STRING: BRD Data Center
[admin@localhost ~]$
If anyone knows the SNMP OIDs for smoke and leak it would be appreciated.
Comments
"Smoke" is set up on "Input 1" per your diagrams but the mibbrowser does not show anything for Smoke or Input 1.
Smoke - Input1name: 172.16.170.9 .1.3.6.1.4.1.17095.1010.13.1.0
Smoke - Input1Value: .1.3.6.1.4.1.17095.6.2.0 "OK" or
FLOOD
Flooding1 - sensor13Name: .1.3.6.1.4.1.17095.11.13.1.0 "Flooding1"
Flooding1 - sensor13value: .1.3.6.1.4.1.17095.11.13.2.0 "WET" or "DRY"