Output not triggering when in alarm exist
Hi All,
I have the gateway HW V5.1 and FW V8.6. The current temp in the room is 28. the down range is set to >25. The status shows alarm, however the output has not activated. If i change the down range for example >30 then warm the temp up on the sensor it will trigger the output.
Im just confused to why the output will not activate if the sensor is already in alarm when setting values.
This issue has put me off from installing in 4 of our server rooms.
Any help appreciated.
Thanks,!
I have the gateway HW V5.1 and FW V8.6. The current temp in the room is 28. the down range is set to >25. The status shows alarm, however the output has not activated. If i change the down range for example >30 then warm the temp up on the sensor it will trigger the output.
Im just confused to why the output will not activate if the sensor is already in alarm when setting values.
This issue has put me off from installing in 4 of our server rooms.
Any help appreciated.
Thanks,!
Comments
You can play around the numbers more efficiently by going to the calibration menu in your settings page.
That way you dont have to warm up the room, you can add/offset the values of your temperature to simulate an alert.
Also make sure the output device fits the power supply limitation of the SensorHub otherwise you can use the Relay ports instead of the output.
Thanks for your reply! I have done some more testing and can confirm the following. I currently have nothing attached to the relay.
- temp currently 25 degrees and alarm setpoint is greater than 28. If room (or i change numbers in calibration) to work up over 28 degrees. Status goes into alarm and triggers relay.
- temp currently 25 degrees and alarm is not currently in alarm. If i then change the alarm setpoint for example to greater than 24 degrees. Status shows alarm but relay will not trigger.
Surely I'm not the only one with this issue
Thanks Administrator for your acknowledgement, I will await your reply. Just so you know same issue in FWv8.5.