Sensor Expansion Hub
I realized a relay was not triggering on an expansion hub after a sensor was being triggered on one of my gateways. I ended up testing all the active gateways w hubs and noticed none of them were triggering. If i were to trigger the sensor or manually cycle the relay the software would show it triggered but the hardware was not switching the NO terminal. I used a meter to verify the NC and C terminal. All the gateways were updated to the latest 8.1 Jul 1 2019 firmware. The hardware version is 5.1.
I did swap one of the hubs with a new one in stock and it ended up working. I will do a test a couple days from now to see if it is still triggering. I find it odd that all the live gateway hubs arent triggering the relay 1 and 2. Please let me know if theres anything i can try.
I did swap one of the hubs with a new one in stock and it ended up working. I will do a test a couple days from now to see if it is still triggering. I find it odd that all the live gateway hubs arent triggering the relay 1 and 2. Please let me know if theres anything i can try.
This discussion has been closed.
Comments
I have used a Temperature and Humidity on my part though.
When you manual trigger it, were you be able to see that it went from OFF to ON? and hear a click sound on the relays?
Also an update on my setup over the weekend, works fine here, as I have set it up with triggering every hour, using relay1 and relay2 version 8.1 Firmware.
I found this on their website version 7.50 http://downloads.serverscheck.com/sensors/HWver5_Fw_Release7_50.BIN
I have the relays connected to an Axis Module P8221. The Axis P8221 is powered up via PoE. It has its own network connection and only connects to the sensor hub via the contact wires.
I am not sure which device you want me to describe for your 2nd question so ill do both. I have tested the exp hub by triggering the water sensor and having the sensor trigger one of the relays. I have also cycled the relays in the software. I tested the relays by using a meter. NC and C seem to work fine but never switches when the relay is triggered. The software shows the relays are ON but don't reflect in the hardware. My test points were not the wires but the green terminals themselves on exp hub.
On relay 1 and 2 on the exp hub the wires are connected to C and NO. Relay 1 of the exp hubs connects to Input 1 of the Axis module and relay 2 connects to Input 2 of the Axis Module. The Axis module then triggers a camera within the area affected as stated in its software parameters.
Thanks.
Relay only triggers auxiliary devices directly connected unto it such as Light Alarm or Sound Alarm.
Could you try a simple light bulb switch relay just to isolate if the issue is in your current set-up configuration or on the SensorHub.
The way we are using the relay is as a simple contact. Once the input on the Axis module sees a closed contact it triggers the video. In this point the relay is directly connected to the axis module.
Update: After replacing a "bad" sensor hub i tested it again and it started working. I left it at rest for about a week.
I have three hubs that appear to be doing exactly the same thing. On the wet out (+12v and the output) goes between 9vDC when "on" and 2.9vDC when "off". When using the dry relay (Ground and the Output) I don't see any change of state. Not sure these things are really up to the job.