Couldnt retrieve value for OID

JohnEastwoodJohnEastwood
I am trying to configure the humidity probe which is attached to the sensor gateway however i am getting this "Couldn't retrieve value for OID" error.



Any ideas?



thanks

Comments

  • AdministratorAdministrator
    Moving this to ServersCheck Monitoring Software section.



    Latest version has this previous bug fixed.
  • JohnEastwoodJohnEastwood
    Hi



    I have upgraded the software to 11.0.2 also i have restarted all three sensor gateway's and the humidity probes are still halted with the error description "Couldn't retrieve value for OID". Is there something else i'm missing? i have set up all the temps and pings and they are reporting back fine.



    Any ideas would be great.



    Thanks
  • AdministratorAdministrator
    Make a new DCIM check and see if that will work
  • JohnEastwoodJohnEastwood
    Hi



    Deleted the existing humidity monitors and re-created them as you have suggested. They are checking but not reporting back a value. the status is now DOWN instead of HALTED. Is there something else i need to do?



    Thanks for your help.
  • AdministratorAdministrator
    What does the error message show?
  • JohnEastwoodJohnEastwood
    Still getting the same error message "Couldn't retrieve value for OID". I have restarted the sensor gateway which i didn't do after i re-created the monitor, but still no joy.
  • AdministratorAdministrator
    We're gonna need a debug output for that. Kindly check out our wiki for instructions on debugging the web server.



    Once on debug, test your settings then stop debugging process. Then give us the output.
  • CrobertsCroberts
    The Temperature oid are now working for me, but the Water sensor oid is not working still saying "could'nt retrieve value for OID"


  • JohnEastwoodJohnEastwood
    Here is some of the info from the debug file. unsure on how to upload the actual text file. hope you can help



    Regards



    John



    # Fri Sep 5 12:31:49 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:31:59 2014 SNMP error 2: Net::SNMP=HASH(0x888cec8)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:31:59 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:32:10 2014 SNMP error 2: Net::SNMP=HASH(0x888cd6c)->error()

    # Fri Sep 5 12:32:10 2014 delete - 1409738776

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:32:10 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:32:20 2014 SNMP error 2: Net::SNMP=HASH(0x888cc88)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:32:20 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:32:30 2014 SNMP error 2: Net::SNMP=HASH(0x887e378)->error()

    # Fri Sep 5 12:32:30 2014 delete - 1409738776

    # Fri Sep 5 12:32:30 2014 Importing current status of each monitor

    # Fri Sep 5 12:32:30 2014 End importing current status of each monitor

    # Fri Sep 5 12:33:19 2014 Reading configuration file - last was 1409916709

    # Fri Sep 5 12:33:19 2014 Reading conf file completed

    # Fri Sep 5 12:33:49 2014 Importing current status of each monitor

    # Fri Sep 5 12:33:49 2014 End importing current status of each monitor

    # Fri Sep 5 12:34:49 2014 Reading configuration file - last was 1409916799

    # Fri Sep 5 12:34:49 2014 Reading conf file completed

    # Fri Sep 5 12:35:19 2014 Importing current status of each monitor

    # Fri Sep 5 12:35:19 2014 End importing current status of each monitor

    # Fri Sep 5 12:36:19 2014 Reading configuration file - last was 1409916889

    # Fri Sep 5 12:36:19 2014 Reading conf file completed

    # Fri Sep 5 12:36:49 2014 Importing current status of each monitor

    # Fri Sep 5 12:36:49 2014 End importing current status of each monitor

    # Fri Sep 5 12:37:49 2014 Reading configuration file - last was 1409916979

    # Fri Sep 5 12:37:49 2014 Reading conf file completed

    # Fri Sep 5 12:38:19 2014 Importing current status of each monitor

    # Fri Sep 5 12:38:19 2014 End importing current status of each monitor

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:38:24 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:38:34 2014 SNMP error 2: Net::SNMP=HASH(0x86dc540)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:38:34 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:38:44 2014 SNMP error 2: Net::SNMP=HASH(0x88750b4)->error()

    # Fri Sep 5 12:38:44 2014 delete - 1409738776

    # Fri Sep 5 12:38:44 2014 team: - SS6610CC<X><X><X><X>SensorGateway2<X>DRSERVERROOM<X>Public<X>1.3.6.1.4.1.17095.3.10.0<X>

    # Fri Sep 5 12:38:44 2014 application:<X>

    # Fri Sep 5 12:38:44 2014 wapplication:<X>

    # Fri Sep 5 12:38:44 2014 team2: - # Fri Sep 5 12:38:44 2014 storing by line

    # Fri Sep 5 12:38:44 2014 storing by uid 1409738776

    11

    # Fri Sep 5 12:38:44 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:38:44 2014 Reading conf file completed

    # Fri Sep 5 12:38:44 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:38:44 2014 Reading conf file completed

    # Fri Sep 5 12:38:44 2014 team: - SS6610CC<X><X><X><X>SensorGateway2<X>DRSERVERROOM<X>Public<X>1.3.6.1.4.1.17095.3.10.0<X>

    # Fri Sep 5 12:38:44 2014 application:<X>

    # Fri Sep 5 12:38:44 2014 wapplication:<X>

    # Fri Sep 5 12:38:44 2014 team2: - # Fri Sep 5 12:38:44 2014 storing by line

    # Fri Sep 5 12:38:44 2014 storing by uid 1409738776

    11

    # Fri Sep 5 12:38:44 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:38:44 2014 Reading conf file completed

    # Fri Sep 5 12:38:44 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:38:44 2014 Reading conf file completed

    # Fri Sep 5 12:38:44 2014 team: - SS6610CC<X><X><X><X>SensorGateway2<X>DRSERVERROOM<X>Public<X>1.3.6.1.4.1.17095.3.10.0<X>

    # Fri Sep 5 12:38:44 2014 application:<X>

    # Fri Sep 5 12:38:44 2014 wapplication:<X>

    # Fri Sep 5 12:38:44 2014 team2: - # Fri Sep 5 12:38:44 2014 storing by line

    # Fri Sep 5 12:38:44 2014 storing by uid 1409738776

    11

    # Fri Sep 5 12:38:44 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:38:44 2014 Reading conf file completed

    # Fri Sep 5 12:38:44 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:38:44 2014 Reading conf file completed



    HUMIDITY

    C:serverscheck_databasesrrdtool.exe graph "C:Program Files (x86)ServersCheck_Monitoring/outputgraphs1409738776HUMIDITY-value.gif" -u 1 -h 200 -w 500 -v "% relative humidity" -t "HUMIDITY - HUMIDITY (DRSERVERROOM)" DEF:line1=C:serverscheck_databases1409738776HUMIDITY-value.rrd:response:MAX LINE1:line1#FF9933:"" GPRINT:line1:MIN:"Min %.2lf" GPRINT:line1:MAX:"Max %.2lf" GPRINT:line1:AVERAGE:"Avg %.2lf" GPRINT:line1:LAST:"Last %.2lfn" COMMENT:n COMMENT:n COMMENT:"" COMMENT:"Graph created on Fri Sep 5 12:38:44 2014 by ServersCheck Freeware Edition"

    # Fri Sep 5 12:38:44 2014 1409738776HUMIDITY - Graph plotting: 597x293

    # Fri Sep 5 12:38:44 2014 Logs from 1409871600:Fri Sep 5 00:00:00 2014 to 1409958000:Sat Sep 6 00:00:00 2014

    # Fri Sep 5 12:38:44 2014 Scanning log: alerts-2014-9-5

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:38:45 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:38:55 2014 SNMP error 2: Net::SNMP=HASH(0x88746dc)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:38:55 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:39:05 2014 SNMP error 2: Net::SNMP=HASH(0x887e48c)->error()

    # Fri Sep 5 12:39:05 2014 delete - 1409738776

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:39:05 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:39:15 2014 SNMP error 2: Net::SNMP=HASH(0x888ccf4)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:39:15 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:39:25 2014 SNMP error 2: Net::SNMP=HASH(0x86efb90)->error()

    # Fri Sep 5 12:39:25 2014 delete - 1409738776

    # Fri Sep 5 12:39:27 2014 Importing current status of each monitor

    # Fri Sep 5 12:39:27 2014 End importing current status of each monitor

    # Fri Sep 5 12:39:33 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:39:33 2014 Reading conf file completed

    # Fri Sep 5 12:39:37 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:39:37 2014 Reading conf file completed



    HUMIDITY

    C:serverscheck_databasesrrdtool.exe graph "C:Program Files (x86)ServersCheck_Monitoring/outputgraphs1409738776HUMIDITY-value.gif" -u 1 -h 200 -w 500 -v "% relative humidity" -t "HUMIDITY - HUMIDITY (DRSERVERROOM)" DEF:line1=C:serverscheck_databases1409738776HUMIDITY-value.rrd:response:MAX LINE1:line1#FF9933:"" GPRINT:line1:MIN:"Min %.2lf" GPRINT:line1:MAX:"Max %.2lf" GPRINT:line1:AVERAGE:"Avg %.2lf" GPRINT:line1:LAST:"Last %.2lfn" COMMENT:n COMMENT:n COMMENT:"" COMMENT:"Graph created on Fri Sep 5 12:39:40 2014 by ServersCheck Freeware Edition"

    # Fri Sep 5 12:39:40 2014 1409738776HUMIDITY - Graph plotting: 597x293

    # Fri Sep 5 12:39:41 2014 Logs from 1409871600:Fri Sep 5 00:00:00 2014 to 1409958000:Sat Sep 6 00:00:00 2014

    # Fri Sep 5 12:39:41 2014 Scanning log: alerts-2014-9-5

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:39:42 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:39:52 2014 SNMP error 2: Net::SNMP=HASH(0x888cde4)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:39:52 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:40:02 2014 SNMP error 2: Net::SNMP=HASH(0x8874544)->error()

    # Fri Sep 5 12:40:02 2014 delete - 1409738776

    # Fri Sep 5 12:40:16 2014 team: - SS6610CC<X><X><X><X>SensorGateway2<X>DRSERVERROOM<X>Public<X>1.3.6.1.4.1.17095.3.10.0<X>

    # Fri Sep 5 12:40:16 2014 application:<X>

    # Fri Sep 5 12:40:16 2014 wapplication:<X>

    # Fri Sep 5 12:40:16 2014 team2: - # Fri Sep 5 12:40:16 2014 storing by line

    # Fri Sep 5 12:40:16 2014 storing by uid 1409738776

    11

    # Fri Sep 5 12:40:16 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:40:16 2014 Reading conf file completed

    # Fri Sep 5 12:40:16 2014 Reading configuration file - last was 0

    # Fri Sep 5 12:40:16 2014 Reading conf file completed



    HUMIDITY

    C:serverscheck_databasesrrdtool.exe graph "C:Program Files (x86)ServersCheck_Monitoring/outputgraphs1409738776HUMIDITY-value.gif" -u 1 -h 200 -w 500 -v "% relative humidity" -t "HUMIDITY - HUMIDITY (DRSERVERROOM)" DEF:line1=C:serverscheck_databases1409738776HUMIDITY-value.rrd:response:MAX LINE1:line1#FF9933:"" GPRINT:line1:MIN:"Min %.2lf" GPRINT:line1:MAX:"Max %.2lf" GPRINT:line1:AVERAGE:"Avg %.2lf" GPRINT:line1:LAST:"Last %.2lfn" COMMENT:n COMMENT:n COMMENT:"" COMMENT:"Graph created on Fri Sep 5 12:40:16 2014 by ServersCheck Freeware Edition"

    # Fri Sep 5 12:40:16 2014 1409738776HUMIDITY - Graph plotting: 597x293

    # Fri Sep 5 12:40:17 2014 Logs from 1409871600:Fri Sep 5 00:00:00 2014 to 1409958000:Sat Sep 6 00:00:00 2014

    # Fri Sep 5 12:40:17 2014 Scanning log: alerts-2014-9-5

    # Fri Sep 5 12:40:20 2014 Redirect 3

    # Fri Sep 5 12:40:30 2014 Importing current status of each monitor

    # Fri Sep 5 12:40:30 2014 End importing current status of each monitor



    HUMIDITY

    C:serverscheck_databasesrrdtool.exe graph "C:Program Files (x86)ServersCheck_Monitoring/outputgraphs1409738776HUMIDITY-value.gif" -u 1 -h 200 -w 500 -v "% relative humidity" -t "HUMIDITY - HUMIDITY (DRSERVERROOM)" DEF:line1=C:serverscheck_databases1409738776HUMIDITY-value.rrd:response:MAX LINE1:line1#FF9933:"" GPRINT:line1:MIN:"Min %.2lf" GPRINT:line1:MAX:"Max %.2lf" GPRINT:line1:AVERAGE:"Avg %.2lf" GPRINT:line1:LAST:"Last %.2lfn" COMMENT:n COMMENT:n COMMENT:"" COMMENT:"Graph created on Fri Sep 5 12:40:30 2014 by ServersCheck Freeware Edition"

    # Fri Sep 5 12:40:30 2014 1409738776HUMIDITY - Graph plotting: 597x293

    # Fri Sep 5 12:40:31 2014 Logs from 1409871600:Fri Sep 5 00:00:00 2014 to 1409958000:Sat Sep 6 00:00:00 2014

    # Fri Sep 5 12:40:31 2014 Scanning log: alerts-2014-9-5

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:40:32 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:40:42 2014 SNMP error 2: Net::SNMP=HASH(0x887e474)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:40:42 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:40:52 2014 SNMP error 2: Net::SNMP=HASH(0x888d054)->error()

    # Fri Sep 5 12:40:52 2014 delete - 1409738776

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:40:52 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:41:02 2014 SNMP error 2: Net::SNMP=HASH(0x888d168)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:41:02 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:41:12 2014 SNMP error 2: Net::SNMP=HASH(0x888c754)->error()

    # Fri Sep 5 12:41:12 2014 delete - 1409738776

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:41:12 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:41:22 2014 SNMP error 2: Net::SNMP=HASH(0x4ecf9c4)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:41:22 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:41:33 2014 SNMP error 2: Net::SNMP=HASH(0x86f8a64)->error()

    # Fri Sep 5 12:41:33 2014 delete - 1409738776

    # Fri Sep 5 12:41:33 2014 Reading configuration file - last was 1409917216

    # Fri Sep 5 12:41:33 2014 Reading conf file completed

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:41:33 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:41:43 2014 SNMP error 2: Net::SNMP=HASH(0x887e3fc)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:41:43 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:41:53 2014 SNMP error 2: Net::SNMP=HASH(0x888cafc)->error()

    # Fri Sep 5 12:41:53 2014 delete - 1409738776

    connection: SensorGateway2

    1.3.6.1.4.1.17095.3

    # Fri Sep 5 12:41:53 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:42:03 2014 SNMP error 2: Net::SNMP=HASH(0x86dc4f8)->error()

    1.3.6.1.4.1.17095.11

    # Fri Sep 5 12:42:03 2014 SNMP WALK trying v1 on DRSERVERROOM 161 Public

    # Fri Sep 5 12:42:13 2014 SNMP error 2: Net::SNMP=HASH(0x8874a78)->error()

    # Fri Sep 5 12:42:13 2014 delete - 1409738776

    # Fri Sep 5 12:42:13 2014 Importing current status of each monitor

    # Fri Sep 5 12:42:13 2014 End importing current status of each monitor

    # Fri Sep 5 12:43:36 2014 Reading configuration file - last was 1409917293

    # Fri Sep 5 12:43:36 2014 Reading conf file completed

    # Fri Sep 5 12:43:36 2014 Importing current status of each monitor

    # Fri Sep 5 12:43:36 2014 End importing current status of each monitor
  • AdministratorAdministrator
    We need to pass this on to our development team to get additional debugging information included in the code.
  • JohnEastwoodJohnEastwood
    Thats great



    Thanks :)
  • AdministratorAdministrator
    Croberts,

    Create a new check and see if it'll work
  • JohnEastwoodJohnEastwood
    Any news from your developers in regard to this debug file i sent you?



    Regards



    John
  • AdministratorAdministrator
    It is in the development queue.



    Allow me to explain how our development queue is processed. Each request (including yours) gets a weight next to it. The weight is computation based on:

    - freeware or paid licenses

    - number of licenses requesting the feature

    - level of urgency as determined by development



    Priorities may shift depending on new requests and their weight.



    It will be done but we can't commit to specific timings.
This discussion has been closed.