False alerts after 10.3.1
After upgrading to 10.3.1 from 10.2.0, Serverscheck keeps reporting all of our websites and VMware hosts are down when they are in fact up and running perfectly fine and the Test Settings button consistently returns OK for all the monitors. We've tried to reboot Serverscheck box twice now. Deleting and recreating the monitor hasn't fixed the issue. Please help.
The specific errors are:
Website URL content monitor - 500 Status read failed - Unknown error
VMware host health monitor - Could not connect VMware ESX server
The specific errors are:
Website URL content monitor - 500 Status read failed - Unknown error
VMware host health monitor - Could not connect VMware ESX server
This discussion has been closed.
Comments
If confirmed, kindly do a debug on the monitoring manager as indicated on the following link and inform us of the log during the time that ServersCheck detected it as down.
http://wiki.serverscheck.com/index.php/Monitoring_debug
It appears to be happening to all (and only) our https checks. If the check is edited to http, the check turns to OK. Change it back to https and it goes down again.
The https pages can be seen on a browser if logged in to the serverscheck machine using the same account the service runs as, so there's no firewall or permissions issue. Also the checks were working immediately prior to the upgrade.
PS. I work with Zixun.
Please reply with the debug mode
In 10.3.1 nothing was changed for the HTTPS or HTTP check
# S-X Tue Dec 17 10:34:49 2013 Starting URL check for 1265580343URL
# S-X Tue Dec 17 10:34:49 2013 Error: 500 Status read failed: Unknown error
# S-X Tue Dec 17 10:34:49 2013 graph day time (0)for 1202172266URL reset to current
# S-X Tue Dec 17 10:34:49 2013 graph week time for 1202172266URL reset to current
# S-X Tue Dec 17 10:34:49 2013 1202172266URL Day Graphs Debug - Refresh rate: 300 - Drawgraphs:1 - 1:Last at 1387229689 (1387229689)
# S-X Tue Dec 17 10:34:49 2013 skipping Availability graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 skipping SLA graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1202172266URL-value.rrd 1387229689:500
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1202172266URL-response.rrd 1387229689:0
# S-1 Tue Dec 17 10:34:49 2013 1202172266URL - DOWN - 500 Status read failed: Unknown error
# S-1 Tue Dec 17 10:34:49 2013 save 1202172266URL<!!>1387229689<!!>205417<!!>0<!!>1386888123<!!>
# S-1 Tue Dec 17 10:34:49 2013 1202172266URL - s:DOWN - e:500 Status read failed: Unknown error - v:0 - t:1387229689
# S-X Tue Dec 17 10:34:49 2013 Error: 500 Status read failed: Unknown error
# S-X Tue Dec 17 10:34:49 2013 Error: 500 Status read failed: Unknown error
# S-X Tue Dec 17 10:34:49 2013 graph day time (0)for 1217557737URL reset to current
# S-X Tue Dec 17 10:34:49 2013 graph week time for 1217557737URL reset to current
# S-X Tue Dec 17 10:34:49 2013 1217557737URL Day Graphs Debug - Refresh rate: 300 - Drawgraphs:1 - 1:Last at 1387229689 (1387229689)
# S-X Tue Dec 17 10:34:49 2013 Error: 500 Status read failed: Unknown error
# S-X Tue Dec 17 10:34:49 2013 skipping Availability graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 skipping SLA graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1217557737URL-value.rrd 1387229689:500
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1217557737URL-response.rrd 1387229689:0
# S-4 Tue Dec 17 10:34:49 2013 1217557737URL - DOWN - 500 Status read failed: Unknown error
# S-4 Tue Dec 17 10:34:49 2013 save 1217557737URL<!!>1387229689<!!>207631<!!>0<!!>1386887989<!!>
# S-4 Tue Dec 17 10:34:49 2013 1217557737URL - s:DOWN - e:500 Status read failed: Unknown error - v:0 - t:1387229689
# S-X Tue Dec 17 10:34:49 2013 graph day time (0)for 1225763477URL reset to current
# S-X Tue Dec 17 10:34:49 2013 graph week time for 1225763477URL reset to current
# S-X Tue Dec 17 10:34:49 2013 1225763477URL Day Graphs Debug - Refresh rate: 300 - Drawgraphs:1 - 1:Last at 1387229689 (1387229689)
# S-X Tue Dec 17 10:34:49 2013 skipping Availability graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 skipping SLA graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1225763477URL-value.rrd 1387229689:500
# S-X Tue Dec 17 10:34:49 2013 graph day time (0)for 1266290093URL reset to current
# S-X Tue Dec 17 10:34:49 2013 graph week time for 1266290093URL reset to current
# S-X Tue Dec 17 10:34:49 2013 1266290093URL Day Graphs Debug - Refresh rate: 300 - Drawgraphs:1 - 1:Last at 1387229689 (1387229689)
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1225763477URL-response.rrd 1387229689:0
# S-5 Tue Dec 17 10:34:49 2013 1225763477URL - DOWN - 500 Status read failed: Unknown error
# S-X Tue Dec 17 10:34:49 2013 skipping Availability graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 skipping SLA graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1266290093URL-value.rrd 1387229689:500
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1266290093URL-response.rrd 1387229689:0
# S-5 Tue Dec 17 10:34:49 2013 save 1225763477URL<!!>1387229689<!!>163019<!!>0<!!>1387156088<!!>
# S-5 Tue Dec 17 10:34:49 2013 1225763477URL - s:DOWN - e:500 Status read failed: Unknown error - v:0 - t:1387229689
# S-2 Tue Dec 17 10:34:49 2013 1266290093URL - DOWN - 500 Status read failed: Unknown error
# S-2 Tue Dec 17 10:34:49 2013 save 1266290093URL<!!>1387229689<!!>51035<!!>0<!!>1386888476<!!>
# S-2 Tue Dec 17 10:34:49 2013 1266290093URL - s:DOWN - e:500 Status read failed: Unknown error - v:0 - t:1387229689
# S-X Tue Dec 17 10:34:49 2013 Error: 500 Status read failed: Unknown error
# S-X Tue Dec 17 10:34:49 2013 Error: 500 Status read failed: Unknown error
# S-X Tue Dec 17 10:34:49 2013 Error: 500 Status read failed: File exists
# S-X Tue Dec 17 10:34:49 2013 Error: 500 Status read failed: Unknown error
# S-X Tue Dec 17 10:34:49 2013 graph day time (0)for 1265581486URL reset to current
# S-X Tue Dec 17 10:34:49 2013 graph week time for 1265581486URL reset to current
# S-X Tue Dec 17 10:34:49 2013 1265581486URL Day Graphs Debug - Refresh rate: 300 - Drawgraphs:1 - 1:Last at 1387229689 (1387229689)
# S-X Tue Dec 17 10:34:49 2013 skipping Availability graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 skipping SLA graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1265581486URL-value.rrd 1387229689:500
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1265581486URL-response.rrd 1387229689:0
# S-0 Tue Dec 17 10:34:49 2013 1265581486URL - DOWN - 500 Status read failed: File exists
# S-X Tue Dec 17 10:34:49 2013 graph day time (0)for 1241746331URL reset to current
# S-X Tue Dec 17 10:34:49 2013 graph week time for 1241746331URL reset to current
# S-X Tue Dec 17 10:34:49 2013 1241746331URL Day Graphs Debug - Refresh rate: 300 - Drawgraphs:1 - 1:Last at 1387229689 (1387229689)
# S-X Tue Dec 17 10:34:49 2013 skipping Availability graphs - only value graphs plotted (true - 1 - 1)
# S-0 Tue Dec 17 10:34:49 2013 save 1265581486URL<!!>1387229689<!!>48047<!!>0<!!>1387155480<!!>
# S-X Tue Dec 17 10:34:49 2013 skipping SLA graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1241746331URL-value.rrd 1387229689:500
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1241746331URL-response.rrd 1387229689:0
# S-0 Tue Dec 17 10:34:49 2013 1265581486URL - s:DOWN - e:500 Status read failed: File exists - v:0 - t:1387229689
# S-6 Tue Dec 17 10:34:49 2013 1241746331URL - DOWN - 500 Status read failed: Unknown error
# S-6 Tue Dec 17 10:34:49 2013 save 1241746331URL<!!>1387229689<!!>270459<!!>0<!!>1386887719<!!>
# S-6 Tue Dec 17 10:34:49 2013 1241746331URL - s:DOWN - e:500 Status read failed: Unknown error - v:0 - t:1387229689
# S-X Tue Dec 17 10:34:49 2013 graph day time (0)for 1290655856URL reset to current
# S-X Tue Dec 17 10:34:49 2013 graph week time for 1290655856URL reset to current
# S-X Tue Dec 17 10:34:49 2013 1290655856URL Day Graphs Debug - Refresh rate: 300 - Drawgraphs:1 - 1:Last at 1387229689 (1387229689)
# S-X Tue Dec 17 10:34:49 2013 skipping Availability graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 skipping SLA graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1290655856URL-value.rrd 1387229689:500
# S-X Tue Dec 17 10:34:49 2013 update C:serverscheck_databases1290655856URL-response.rrd 1387229689:0
# S-8 Tue Dec 17 10:34:49 2013 1290655856URL - DOWN - 500 Status read failed: Unknown error
# S-8 Tue Dec 17 10:34:49 2013 save 1290655856URL<!!>1387229689<!!>61436<!!>0<!!>1386888131<!!>
# S-8 Tue Dec 17 10:34:49 2013 1290655856URL - s:DOWN - e:500 Status read failed: Unknown error - v:0 - t:1387229689
# S-X Tue Dec 17 10:34:50 2013 Error: 500 Status read failed: Unknown error
# S-X Tue Dec 17 10:34:50 2013 graph day time (0)for 1265580343URL reset to current
# S-X Tue Dec 17 10:34:50 2013 graph week time for 1265580343URL reset to current
# S-X Tue Dec 17 10:34:50 2013 1265580343URL Day Graphs Debug - Refresh rate: 300 - Drawgraphs:1 - 1:Last at 1387229690 (1387229690)
# S-X Tue Dec 17 10:34:50 2013 skipping Availability graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:50 2013 skipping SLA graphs - only value graphs plotted (true - 1 - 1)
# S-X Tue Dec 17 10:34:50 2013 update C:serverscheck_databases1265580343URL-value.rrd 1387229690:500
# S-X Tue Dec 17 10:34:50 2013 update C:serverscheck_databases1265580343URL-response.rrd 1387229690:0
# S-10 Tue Dec 17 10:34:50 2013 1265580343URL - DOWN - 500 Status read failed: Unknown error
# S-10 Tue Dec 17 10:34:50 2013 save 1265580343URL<!!>1387229690<!!>93538<!!>0<!!>1386888806<!!>
# S-10 Tue Dec 17 10:34:50 2013 1265580343URL - s:DOWN - e:500 Status read failed: Unknown error - v:0 - t:1387229690
# S-1 Tue Dec 17 10:34:50 2013 1202172266URL - finished in 2 sec
# S-1 Tue Dec 17 10:34:50 2013 1202172266URL - didn't time out
# S-1 Tue Dec 17 10:34:50 2013 1266289718URL - setting Threadcheckstarted for thread S-1 to 1387229690 - stored:1387229690
# S-1 Tue Dec 17 10:34:50 2013 1266289718URL - Starting check - 132401
Event Type: Error
Event Source: Application Error
Event Category: (100)
Event ID: 1000
Date: 13/12/2013
Time: 3:45:58 p.m.
User: N/A
Computer: SERVERSCHECK
Description:
Faulting application monitoring_thread2.exe, version 10.0.0.0, faulting module rrds.dll, version 0.0.0.0, fault address 0x0006b4fb.
For more information, see Help and Support Center at http://go.microsoft.com/fwlink/events.asp.
Data:
0000: 41 70 70 6c 69 63 61 74 Applicat
0008: 69 6f 6e 20 46 61 69 6c ion Fail
0010: 75 72 65 20 20 6d 6f 6e ure mon
0018: 69 74 6f 72 69 6e 67 5f itoring_
0020: 74 68 72 65 61 64 32 2e thread2.
0028: 65 78 65 20 31 30 2e 30 exe 10.0
0030: 2e 30 2e 30 20 69 6e 20 .0.0 in
0038: 72 72 64 73 2e 64 6c 6c rrds.dll
0040: 20 30 2e 30 2e 30 2e 30 0.0.0.0
0048: 20 61 74 20 6f 66 66 73 at offs
0050: 65 74 20 30 30 30 36 62 et 0006b
0058: 34 66 62 4fb
We need the output of the web server in debug mode:
http://wiki.serverscheck.com/index.php/Webserver_debug
# Tue Dec 17 11:05:14 2013 file 10.1.1.150.scanc cleaned
# Tue Dec 17 11:05:14 2013 file events.log cleaned
# Tue Dec 17 11:05:14 2013 file master.log cleaned
# Tue Dec 17 11:05:14 2013 file ready.scan cleaned
# Tue Dec 17 11:05:14 2013 file (removed).scanc cleaned
# Tue Dec 17 11:05:14 2013 file (removed).scanc cleaned
# Tue Dec 17 11:05:14 2013 file (removed).scanc cleaned
# Tue Dec 17 11:05:14 2013 file (removed).scanc cleaned
# Tue Dec 17 11:05:14 2013 file (removed).scanc cleaned
# Tue Dec 17 11:05:14 2013 file (removed).scanc cleaned
# Tue Dec 17 11:05:14 2013 file (removed).scanc cleaned
# Tue Dec 17 11:05:14 2013 file (removed).scanc cleaned
# Tue Dec 17 11:05:14 2013 file (removed).scanc cleaned
# Tue Dec 17 11:05:14 2013 file test.log cleaned
#
# ServersCheck Web Server
# Monitoring Appliance - BUSINESS 250 Edition
# ServersCheck Appliance - BUSINESS 250 Edition - version 10.3.1
#
# Number of monitors allowed: 250
#
# Installed on 10.1.1.250 - SERVERSCHECK
#
# Loading language file: EN.lang
# version 10.3.1
#
#
# (c) Copyright 2003-2013 - ServersCheck BVBA
# www.serverscheck.com
#
#
#
#
#
# Start: Tue Dec 17 11:05:14 2013 - End: Tue Dec 17 11:05:15 2013
#
# Configuration server ready, serving on port "1272"...
#
#
# Tue Dec 17 11:05:16 2013 monitor - (removed) - /checks.html - login FAILED
# no data to decrypt
# Tue Dec 17 11:05:16 2013 monitor - (removed) - /checks.html - login OK
# no data to decrypt
# Tue Dec 17 11:05:16 2013 monitor - (removed) - /checks.html - login FAILED
# Tue Dec 17 11:05:16 2013 Reading configuration file - last was
# Tue Dec 17 11:05:16 2013 Reading conf file completed
# Tue Dec 17 11:05:16 2013 Importing current status of each monitor
# Tue Dec 17 11:05:16 2013 End importing current status of each monitor
# Tue Dec 17 11:05:25 2013 Administrator - (removed) - /ajax_stats1.html
# Tue Dec 17 11:05:25 2013 Administrator - (removed) - /ajax_stats1.html
# Tue Dec 17 11:05:37 2013 Administrator - (removed) - /ajax_stats1.html
# Tue Dec 17 11:05:39 2013 Administrator - (removed) - /ajax_checks.html
URL
C:serverscheck_databasesrrdtool.exe graph "C:Program FilesServersCheck_Monitoring/outputgraphs1386797324URL-response.gif" -u 1 -h 200 -w 500 -v "Page download time in ms" -t "URL - Page download time in ms" DEF:line1=C:serverscheck_databases1386797324URL-response.rrd:response:MAX LINE1:line1#FF9933:"Page download time in ms" GPRINT:line1:MIN:"Min %.2lf" GPRINT:line1:MAX:"Max %.2lf" GPRINT:line1:AVERAGE:"Avg %.2lf" GPRINT:line1:LAST:"Last %.2lfn" COMMENT:n COMMENT:n COMMENT:"" COMMENT:"Graph created on Tue Dec 17 11:05:43 2013 by ServersCheck Appliance"
# Tue Dec 17 11:05:44 2013 1386797324URL - Graph plotting: 597x293
URL
C:serverscheck_databasesrrdtool.exe graph "C:Program FilesServersCheck_Monitoring/outputgraphs1386797324URL-value.gif" -u 1 -h 200 -w 500 -v "HTTP Status code" -t "URL - HTTP Status code" DEF:line1=C:serverscheck_databases1386797324URL-value.rrd:response:MAX LINE1:line1#FF9933:"HTTP Status code" GPRINT:line1:MIN:"Min %.2lf" GPRINT:line1:MAX:"Max %.2lf" GPRINT:line1:AVERAGE:"Avg %.2lf" GPRINT:line1:LAST:"Last %.2lfn" COMMENT:n COMMENT:n COMMENT:"" COMMENT:"Graph created on Tue Dec 17 11:05:43 2013 by ServersCheck Appliance"
# Tue Dec 17 11:05:44 2013 1386797324URL - Graph plotting: 597x293
# Tue Dec 17 11:05:44 2013 Logs from 1387191600:Tue Dec 17 00:00:00 2013 to 1387278000:Wed Dec 18 00:00:00 2013
# Tue Dec 17 11:05:44 2013 Scanning log: alerts-2013-12-17
# Tue Dec 17 11:05:45 2013 delete - 1386797324
# Tue Dec 17 11:05:48 2013 Serving Wizard 3 in test mode? 1
# Tue Dec 17 11:05:48 2013 Serving Wizard 4
# Tue Dec 17 11:05:55 2013 Serving Wizard 4_1 - 0
# Tue Dec 17 11:05:56 2013 C:Program FilesServersCheck_Monitoring/
# test Tue Dec 17 11:05:56 2013 Starting Monitoring Rule Thread test
# Tue Dec 17 11:05:56 2013 Running in test mode
# test Tue Dec 17 11:05:56 2013 testmode:1
# test Tue Dec 17 11:05:56 2013 TEST - Starting check
<!DOCTYPE html PUBLIC "-//W3C//DTD XHTML 1.0 Transitional//EN" "http://www.w3.org/TR/xhtml1/DTD/xhtml1-transitional.dtd">
<html xmlns="http://www.w3.org/1999/xhtml">
(REMOVED)
</html>
<!-- System Build: 1.0.5081.25428, 2013-11-29 14:07:37 -->
<!-- System Build: 2.0.0.0, 2011-12-26 09:40:47 --># Tue Dec 17 11:05:58 2013 DOWN comparison: 399 (target) > 200 (returned)
# test Tue Dec 17 11:05:58 2013 Graphing? eq true and 0>=300
# Tue Dec 17 11:05:58 2013 NO file TEST - URL
# test Tue Dec 17 11:05:58 2013 TEST - OK - - 2000
# Tue Dec 17 11:06:01 2013 Serving Wizard 4_1 - 1
# Tue Dec 17 11:06:14 2013 monitor - (removed) - /ajax_stats1.html - login FAILED
# no data to decrypt
# Tue Dec 17 11:06:14 2013 monitor - (removed) - /ajax_stats1.html - login OK
# no data to decrypt
# Tue Dec 17 11:06:14 2013 monitor - (removed) - /ajax_stats1.html - login FAILED
# Tue Dec 17 11:06:15 2013 monitor - (removed) - /checks.html - login FAILED
# no data to decrypt
# Tue Dec 17 11:06:15 2013 monitor - (removed) - /checks.html - login OK
# no data to decrypt
# Tue Dec 17 11:06:15 2013 monitor - (removed) - /checks.html - login FAILED
Anyway... We have had to rebuild from scratch. Good 8 hours work.
Does it work now?
It works now, yes.
To be honest, I would have liked better support since we are paying annual fees. OK, yes we are entitled to the newest version in our fees, but in this case the upgrade broke our installation.
At one point I was advised to run the checks in console mode and watch it until the service crash, then quickly read the console. The respose times, apart from on a couple of occasions has been very slow, considering this software monitors our environment! And we have needed to share information publically. We had an email ticket too, but still sometimes over 24 hours before a response, that ended up being 'please reinstall'. If you're arguement is that the fees are cheap, create a premium support agreement, with real SLA's and phone support.
And one last thing, although yes it's a pain, but IE is very popular browser, please add support for it both on the serverscheck console, and the serverscheck website.
Thank you.
http://wiki.serverscheck.com/index.php/Backup_Configuration_%26_Move
We have a premium support available as part of the PREMIUM edition of the software. The purchase was made by your company for the entry level with basic support. One has a choice at time of purchase.
The fact that a clean install made it work again shows that it wasn't the software but something else that broke it. An upgrade merely replaces exe files and doesn't change anything else.
It is always recommend (and common best practice in the IT industry) to test an upgrade prior to putting it into production, especially if it is critical like you state. For example if you have it installed on a VM Ware server, you can take a snaphost of the server before doing the upgrade and if you have an issue, you can easily roll back.
Not sure if you are running any Antivirus software on that system but if you do, then you might have experienced what has happened to other customers in the past. As a component changes, the AV no longer trusts it and can block network access for it. This would happen after an upgrade.
So we opted to start from scratch.
We don't get the option of premium support. And we don't want/need more that 250 checks at this stage.
I disagree. I think the upgrade did break it, nothing else is installed on that machine and the upgrade was the only thing that was done! I have a feeling the data had been upgraded so many times, that it finally became corrupted for 10.3. I'm going to dump the new conf folder in to the old machine and see what happens.
I should have taken a shopshot but didn't in this case. The upgrade was an attempt to fix another issue on Serverscheck.
We do have AV on it. But definitely not the cause, because we disabled it, and could actually see the packets on our Firewalls, but still marked them as down.
we have the same problem here.
i have updated yesterday to 10.3 and then i had all my esx servers down
is there an other solution then rebuild
aulting application monitoring_thread2.exe, version 10.0.0.0, faulting module ntdll.dll, version 5.2.3790.4937, fault address 0x0002c912.
Could not connect VMWare ESX Server
When i config the monitor the test says ok but then it goes ofline afther a minute
the error message shows that it fails due to a core Windows module ntdll.dll - unfortunately that dll can't be fixed by us.
If you have a second platform available, then try it on there - copy your configuration & database files. If it works then the issue is somewhere at the OS layer or another application running on the host conflicting with our software
so the new update is conflicting with windows cause i didnt change anything to windows no updates or nothing can i do a down grade then
You can try a manual upgrade as detailed in the user manual:
http://wiki.serverscheck.com/index.php/Upgrade
Especially in critical environments we recommend to apply standard best practices in the IT industry meaning to first test a new release and then put it into production.