Humidity Check False Alarm
I have the following warning set:
Set status to WARNING when the humidity is less than 20% or greater than 90% rH
The humidity monitor constantly alters between Warning and Normal with the following error:
Warning level: 85.25 (returned value) less than 90
Why is it that when the warning threshold is set to be greater than 90% rH, I get notified that the level is less than 90? Is this a bug?
Set status to WARNING when the humidity is less than 20% or greater than 90% rH
The humidity monitor constantly alters between Warning and Normal with the following error:
Warning level: 85.25 (returned value) less than 90
Why is it that when the warning threshold is set to be greater than 90% rH, I get notified that the level is less than 90? Is this a bug?
This discussion has been closed.
Comments
http://tinypic.com/r/mux074/5
Topic will be moved to Monitoring Software category
1) Clicking the "Detect Probes"
2) Selecting the designated probe ID
3) Double checking the down and warning alerts configuration
4) Don't forget to save
Warning level: 54.13 (returned value) less than 90
Upon receiving the false warning alarm on humidity (less than 90), you can stop the debug service.
After which, please attach the log file.
https://www.dropbox.com/sh/9mlhqpj90cy4e8l/fTVf3jXcB2
Basing on the debug log, it shows there's a little bit of misconfiguration made on the check specifically on the the warning status configuration.
For that, kindly go to the involved check's configuration window and
1) Select 'Warning Alerts'
2) On the 'Alert when:' section, choose 'All warning and on each status change'
I believe that will solve it. Please do inform us upon applying the recommended workaround.
Thank you.
Warning level: 77.76 (returned value) less than 90