SNMP-Problems after Upgrading to 9.0.18
Hello,
we have a problem after upgrading from 9.0.13 to 9.0.18 with Serverscheck and our APC UPS:
With 9.0.13 the SNMP-Check was OK!
With 9.0.18 we got an error "No numeric value returned (value was: 18 minutes, 00.00)" in the overview and the rule ist "down".
If we click on the Test-Button, we get an OK-Message:
"Der Check wurde ausgeführt.
Status: OK
Zurückgegebener Wert: 18 minutes, 00.00"
The APC UPS check is the batterie-runtime ID ".1.3.6.1.4.1.318.1.1.1.2.2.3.0"
Thanks for help.
Greets pdsrow
we have a problem after upgrading from 9.0.13 to 9.0.18 with Serverscheck and our APC UPS:
With 9.0.13 the SNMP-Check was OK!
With 9.0.18 we got an error "No numeric value returned (value was: 18 minutes, 00.00)" in the overview and the rule ist "down".
If we click on the Test-Button, we get an OK-Message:
"Der Check wurde ausgeführt.
Status: OK
Zurückgegebener Wert: 18 minutes, 00.00"
The APC UPS check is the batterie-runtime ID ".1.3.6.1.4.1.318.1.1.1.2.2.3.0"
Thanks for help.
Greets pdsrow
This discussion has been closed.
Comments
I've updated Serverscheck to 9.1.0 but it didn't solve the problem.
The SNMP OID show now this Value on a test:
"Zurückgegebener Wert: 1080"
The USP runtime should be 18 minutes.
Thanks for your help.
pdsrow
i've found the solution in your release notes:
Update: SNMP check now detects time ticks (regardless of the OID) and converts them into seconds
-> 1080/60 = 18 minutes.
Thanks for your help.
pdsrow