Value for flood show temperature

JennaJenna
edited March 2012 in InfraSensing Sensors
I am using a sensor gateway and the value for my flood is showing as the temperature. I have updated to monitoring software to 9.0.6.



Thanks,



Jenna

Comments

  • AdministratorAdministrator
    A fix is coming in the future for the freeware version



    Currently you have to either create a SNMP check or SNMPSTRING check and use the correct OID. For Flood this would be a SNMPSTRING check



    If you don't know the OID then add the SensorGateway as a new device. Once created, click on SNMP WALK button in the device details page and select the correct OID.
  • JennaJenna
    Is there an estimated time on when there will be a fix?



    THANKS!
  • AdministratorAdministrator
    There is no ETA for freeware users