Upgraded to 8.8.11 - issues

airronairron
edited October 2011 in InfraSensing Sensors
Just upgraded from win 2003 > win 2008 server (new hardware) using bus 500 edition with version 8.8.11. (2) temp sensors ok, (2) power sensor and (1) flood sensor working with tibbo and running ip fine. When look at gui says the power and flood are down? When I perform testing settings > error is > object synchorization method was called from an unsynchronized block of code. What does this error mean? How do I correct? Thanks, Ron

Comments

  • AdministratorAdministrator
    Hello,



    Does the Tibbo report that everything is okay in the device manager? What versions of .NET do you have installed?
  • airronairron
    tibbo ds manager ver. 5.9.5 reports all sensors including power sensors working normally.



    .net versions > v.2.0.50727, v.3.0.30729.4037 , v.3.5.30729.01
  • AdministratorAdministrator
    Hello,



    You will need .NET 1.1 installed, please install that and it should clear your issue up.
  • airronairron
    Yes, you were correct. The 1.1 and then 1.1 SP1 seemed to correct my issue.



    Thank you, Ron