Sensorgatey-Failing after couple of hours
We have 2 sensor gateways (v2, FW 1.2) on our system. They both set up fine and are fully accessible through the web interface. I have followed the set-up instructions, and for the first 4 hours they work fine. Then almost simultaneously they all show as "Down", and report that the OID cannot be read. If I restart the gateways then they go back to normal, and then, after 4 hours, they fail again with the same error. The gateways are on fixed IP addresses and have different MAC addresses. Any suggestions?
This discussion has been closed.
Comments
Gateways at Firmware version 1.2
8.8.3 takes care of this problem. If you have your SensorGateway with default admin / admin settings then you don't need to do anything.
Thanks for your assistance
Neil