Humidity value/sensor
Serverscheck version 7.12.0, environmental sensors only.
Used : T°&Humidity sensor
The humidity warning value is on : less than 10rH or greater than 75rH.
The DOWN values are on : less than 75rH or greater than 80rH.
Warning setup is : "only when warning with a returned value".
PROBLEM : We get always warnings with a returned value as 54,5rH.
But the rH is not less than 10rH and not greater than 75rH.
QUESTION : Why this warning appears always?
Thank you for your answer
Used : T°&Humidity sensor
The humidity warning value is on : less than 10rH or greater than 75rH.
The DOWN values are on : less than 75rH or greater than 80rH.
Warning setup is : "only when warning with a returned value".
PROBLEM : We get always warnings with a returned value as 54,5rH.
But the rH is not less than 10rH and not greater than 75rH.
QUESTION : Why this warning appears always?
Thank you for your answer
This discussion has been closed.
Comments
Your down values are incorrect. The lower limit has to be lower compared to the lower warning limit. 54.5 is always less than 75%rH (lower limit DOWN)
Run the s-server.exe in debug mode and click on test settings. Reply with the output sent.
There is an error in my last post:
The DOWN values are on: less than 10rH or greater than 85rH
How to run s-server.exe in debug mode?
Sincerly,
Here is the result of debug:
# Running in test mode
# test Fri Oct 3 07:41:29 2008 TEST - Starting check
# test Fri Oct 3 07:41:29 2008 C10.1.0.21.log removed (A)
# test Fri Oct 3 07:41:29 2008 COM10.1.0.21 free - starting reading
# Fri Oct 3 07:41:33 2008 Serving Wizard 4_1
# test Fri Oct 3 07:41:35 2008 reading log
# test Fri Oct 3 07:41:36 2008 0 Device Model = Temperature/Humidity Sensor
# test Fri Oct 3 07:41:36 2008 1 Device Status = Normal
# test Fri Oct 3 07:41:36 2008 2 Firmware Version = 5.00
# test Fri Oct 3 07:41:36 2008 3 Number of variables = 5
# test Fri Oct 3 07:41:36 2008 4 Variable 1: HUMIDITY (1 % RESOLUTION) 54 % RH
# test Fri Oct 3 07:41:36 2008 5 Variable 2: HUMIDITY (0.1 % RESOLUTION) 53,9 % RH
# test Fri Oct 3 07:41:36 2008 6 Variable 3: TEMPERATURE (0.5 C RESOLUTION) 22 C
# test Fri Oct 3 07:41:36 2008 7 Variable 4: TEMPERATURE (0.1 C RESOLUTION) 22,1 C
# test Fri Oct 3 07:41:36 2008 8 Variable 5: HASH ID 38031
eq true and 0>=300
# test Fri Oct 3 07:41:36 2008 TEST - OK - - 53.9
# Fri Oct 3 07:41:38 2008 Serving Wizard 4_1
Here is the alert message that I receives:
Thu Oct 2 20:30:48 2008. Motif: Error: Warning level: 53.6 (returned value) greater than 10|75 .
Sincerly,
Please run the sensor against the trial version of latest release of the software (7.14) and report back